Skip to content
C&D Mechanical LLC logo C&D Mechanical LLC Call (603) 724-5600

Spring AC Tune Up: What Is Worth Doing

What a real tune up includes, what you can do yourself in twenty minutes, and how to tell a genuine service from a sticker on the side of the unit.

By Derek Mills, Co-owner, service lead ·

Cooling season here is short. Maybe three months of real work out of the equipment. That short season is exactly why spring service matters more than people assume: the system sits idle for nine months, and things that sit idle develop problems that only show up under load.

The worst day to discover your AC does not work is the first ninety degree day, which is also the day every contractor in the state is booked solid.

What you can do yourself

Rinse the outdoor coil. Kill power at the disconnect first, the box on the wall near the unit. Then a garden hose on low pressure, spraying from the inside out if you can get access, otherwise straight in through the fins. No pressure washer.

Rinse until the water running out is clear. On a unit that has gone a few seasons you will be surprised what comes out.

Clear the surroundings. Two feet on all sides, five overhead. Cut back anything that grew in. If you cover the unit in winter, take the cover off now, and honestly, do not cover them. It traps moisture and gives rodents somewhere nice to live.

Change the filter.

Check the condensate drain. Find the line coming off the indoor unit. Pour a cup of water into the drain pan and confirm it runs out the other end. If it backs up, the line is plugged. Some people pour a little vinegar down annually to keep growth down, which is not a bad habit.

Test it early. Pick a day in April when it is over sixty out, run the cooling for twenty or thirty minutes, and confirm you get cold air and no strange noises. Finding a problem in April means a scheduled repair. Finding it in July means waiting.

What a real service includes

If somebody spends fifteen minutes, hoses the outdoor coil, and leaves a sticker, that was not a tune up.

An actual service should cover:

  • Refrigerant charge verified by measurement, using superheat or subcooling depending on the metering device, not by hooking up gauges and eyeballing a pressure
  • Electrical: capacitor tested against its rating, contactor inspected for pitting, connections checked and tightened, amp draw on the compressor and fan motors compared to nameplate
  • Temperature split across the indoor coil, which tells you whether the system is actually performing
  • Static pressure, which tells you whether the duct system is choking the equipment. Skipped almost universally and it is one of the most useful measurements there is.
  • Blower wheel and evaporator coil inspected, not just the filter
  • Condensate drain flushed and float switch tested
  • Outdoor coil cleaned properly, which sometimes means a coil cleaner rather than water alone

Capacitors are worth calling out. They are cheap, they are the single most common electrical failure in the category, and they degrade measurably before they fail outright. A tech who tests yours and tells you it is reading well below its rating just saved you an emergency call in August.

About maintenance plans

They are worth it if the plan actually gets you a real inspection, priority scheduling in peak season, and a discount on repairs. Priority scheduling in July has genuine value.

They are not worth it if the plan is a filter change and a sticker. Ask what the checklist is and ask whether you get a written report with measured values. A contractor doing real work is happy to show you the numbers.

Timing

April into May, before the first hot stretch. If you can only do one service a year and you have a heat pump, do it in the fall instead, because heating season is the harder duty here and you want it right going into winter.

Related reading

What Counts as an HVAC Emergency

What genuinely needs somebody out tonight, what can wait until morning, and what you should handle yourself before calling anyone.

Derek Mills ·